消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

自动报警系统、排烟系统、灭火系统、安全出口都是准工作状态下,儿童研学教室可以设置在地下一、二层嘛。

自动报警系统、排烟系统、灭火系统、安全出口都是准工作状态下,儿童研学教室可以设置在地下一、二层嘛。

请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

安洪全 2024-08-19 11:32 00 [回复]举报

建筑防火通用规范 GB55037-2022

4.3.4 儿童活动场所的布置应符合下列规定:    

1 不应布置在地下或半地下;    

2 对于一、二级耐火等级建筑,应布置在首层、二层或三层;    

3 对于三级耐火等级建筑,应布置在首层或二层;    

4 对于四级耐火等级建筑,应布置在首层。


条文说明:

本规范规定的“儿童活动场所”是指供12周岁及以下婴幼儿和少儿活动的场所,包括幼儿园、托儿所中供婴幼儿生活和活动的房间,设置在建筑内的儿童游乐厅、儿童乐园、儿童培训班、早教中心等儿童游乐、学习和培训等活动的场所,不包括小学学校的教室等教学场所。有关幼儿园、托儿所中的婴幼儿用房的布置楼层位置要求,还需根据国家现行相关技术标准的规定确定。

关闭

关闭

手机APP下载