消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟风机设置在屋顶,必须设风机房吗?

排烟风机设置在屋顶,必须设风机房吗?谢谢!

葫芦小金刚 | 2024-08-01 18:36
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 6

安洪全 2024-08-02 09:01 00 [回复]举报

LHH2737 2024-08-02 09:17 00 [回复]举报

是的,但也有部分地区(如浙江)允许消防风机露天安装时,,无需设在机房内,设置防雨防虫雨棚即可

知耻也要问 2024-08-02 14:05 00 [回复]举报

规范已经明确了 要是在机房呢 

我头发贼黑 2024-08-02 14:10 00 [回复]举报

14建规以后需要,之前不要求

陈1111 2024-08-03 10:16 00 [回复]举报

潘天坤 2024-08-05 13:35 10 [回复]举报

从国家标准烟标GB51251来说,排烟风机应设置在专用机房内,不过现场不一定具备设置专用机房的条件,有不少地区有技术文件提及室外风机如果有良好的通风、耐候、遮阳、防雨、防火、防雨雪、防堵塞等防护措施可以不设置专用机房,建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准
上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

只有某个楼层设置机械排烟系统,负责该系统的风机可以设置在楼层内的专用排烟机房

如果每个楼层都设置机械排烟系统,那么风机应该设置在屋面的专用排烟机房内(排烟风机宜设置在排烟系统的最高处)



关闭

关闭

手机APP下载