消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

公司目前运行了一套集中控制集中电源型应急照明系统,灯具不自带电源,但灯具是用插头连接的插座,插头拔了灯具是不会亮的,请问是否有规范规定此系统不能用插头连接?

公司目前运行了一套集中控制集中电源型应急照明系统,灯具不自带电源,但灯具是用插头连接的插座,插头拔了灯具是不会亮的,请问是否有规范规定此系统不能用插头连接?(注意是集中控制集中电源型)

l龙的传人 | 2024-07-25 17:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

潘天坤 2024-07-25 23:31 00 [回复]举报

规范没有提及集中电源集中控制型灯具采用插座连接的要求,理论上可以使用

注意插座敷设的线缆的型号、数量应与设计一致,并且不应与强电线路共管敷设

建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准

上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

消防应急照明和疏散指示系统技术标准 GB51309-2018第4.5.5条规定:非集中控制型系统中,自带电源型灯具采用插头连接时,应采用专用工具方可拆卸(条文说明提及:采用自带电源型灯具的非集中控制型系统中,灯具可以采用插头方式连接;但是,为了避免在日常使用过程中非维护人员随意拔出插头,影响灯具的正常运行,插头与插座之间应采取采用专用工具方可拆卸的连接方式连接)

一路同行 2024-07-26 08:37 00 [回复]举报

自带电源、非集中控制可以采用插头连接,但是应采用专用工具拆卸


4.5.5 非集中控制型系统中,自带电源型灯具采用插头连接时,应采用专用工具方可拆卸。

磊中 2024-07-26 08:39 00 [回复]举报

4.5.5 非集中控制型系统中,自带电源型灯具采用插头连接时,应采用专用工具方可拆卸。言外之意其它不可以用插头连接,例如本问题中假如有人为拔掉,在发生火灾的时候就不能起到作用喽

l龙的传人   回复: 磊中2024-08-05 17:32

就是这个意思,为什么规范里已经要求了非集中控制型采用插头要用专用工具,而集中电源、集中控制型国家规范里却没有使用插头的要求,如集中电源型采用插头连接,人为把插头抽了,那岂不是不能发挥作用?

0    0 [回复]举报

南明离火 2024-07-26 11:38 00 [回复]举报

用插头连接 怎么实现集中控制的 切断电源吗

l龙的传人   回复: 南明离火2024-08-05 17:38

有集中控制器,只不过灯具不是用线 直接连接的,而是灯具是与插座连接的

0    0 [回复]举报

花生12138 2024-07-27 16:51 10 [回复]举报

应该不行,只有非集中控制非集中电源的系统才能用插头型的,而且还不能是普通插头,需要是采用专用工具方可拆卸的插头。

甲级防火门 2024-07-29 10:17 00 [回复]举报

你公司采用的是集中电源集中控制的灯具,你把连接插头拔了灯具肯定不会亮啦 。没有电源为它供电。直接把插头改成直接连接一点没病都没有啦。不知道你还在纠结什么?

关闭

关闭

手机APP下载