图纸没明确?? 到底水的系统压力是多少?






关于压力, 图纸只有上图信息,无其他数据了,     涉及到管网强度试验,严密性,冲洗,     请问下,这项目 设计的系统压力,工作压力是多少?????

























知耻也要问 | 2024-07-25 16:28
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

消防网友68723 2024-07-26 10:20 10 [回复]举报

.2.3 高压和临时高压消防给水系统的系统工作压力应根据系统在供水时,可能的最大运行压力确定,并应符合下列规定:
    1 高位消防水池、水塔供水的高压消防给水系统的系统工作压力,应为高位消防水池、水塔最大静压;
    2 市政给水管网直接供水的高压消防给水系统的系统工作压力,应根据市政给水管网的工作压力确定;
    3 采用高位消防水箱稳压的临时高压消防给水系统的系统工作压力,应为消防水泵零流量时的压力与水泵吸水口最大静水压力之和;
    4 采用稳压泵稳压的临时高压消防给水系统的系统工作压力,应取消防水泵零流量时的压力、消防水泵吸水口最大静压二者之和与稳压泵维持系统压力时两者其中的较大值。


磨砂猴 2024-07-26 16:33 20 [回复]举报

系统工作压力1.0Mpa

知耻也要问   回复: 磨砂猴2024-07-31 10:09

怎么判断得出1.0

0    0 [回复]举报

磨砂猴   回复: 知耻也要问2024-08-02 09:21

泵的额定压力是0.7Mpa,最大工作压力是0.98Mpa,水池静压估算0.02Mpa

0    0 [回复]举报