消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

建筑高度为18米的住宅是否需要设置室内消火栓

根据第二款,大于21米的住宅才需要设置室内消火栓;但是第五款,超过15米的民建就需要设置。

如果说超过15米的民建就得设置消火栓,那第二款是不是就应该删掉了?

最帅游客 | 2024-06-21 11:12
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 7

黄-江西省景德镇市 2024-06-21 12:10 00 [回复]举报

第五款里的单、多层建筑不是泛指所有单、多层民用建筑,也不包括住宅,其指的是其他使用功能类似于办公和教学的单、多层建筑。

如果是你理解的那样,那么第三款体积大于5000m³的... ...等单、多层建筑,是不是也包含了住宅呢?

安洪全 2024-06-21 13:06 00 [回复]举报

首先,不应引用“建筑设计防火规范 GB50016-2014(2018年版)-8.2.1”之规定,而是“建筑防火通用规范 GB55037-2022-8.1.7


其次,这两条不冲突,说的是两种不同建筑。

住宅建筑属于民用建筑范畴,但民用建筑不仅只有住宅建筑,还有公共建筑。


消防网友78193 2024-06-21 13:33 00 [回复]举报

我也有相同的疑问

香.香 2024-06-21 13:41 00 [回复]举报

大21米的住宅应设室内消火栓,18米不需要设置。第五条大15米或体积大1万的其它单、多层建筑是指类似于办公、教学建筑类的公共建筑,不包含住宅哈。

最帅游客   回复: 香.香2024-06-21 13:46

好的,谢谢

0    0 [回复]举报

潘天坤 2024-06-21 15:39 00 [回复]举报

第2款已经规定了住宅的要求,第5款这个其他可能有点争议

个人想法:建规和建筑防火通用规范中关于住宅建筑室内消火栓的设置,其他中不含住宅建筑,以大于21米为准

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

shawu 2024-06-23 07:24 01 [回复]举报

建筑高度为18米的住宅如果体积没超1万立不需要设置室内消火栓

关闭

关闭

手机APP下载