消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于常高压消防系统问题

一个小区,楼高度均相同,在每栋楼屋顶设置一个高位消防水箱,使总消防储水量满足总消防用水量。并在其中一栋楼顶设置一个稳压系统。再用环管与地库及商业的消火栓及喷淋系统形成环状管网,这样的系统是不是就能成为常高压消防系统。从而取消地下室消防泵房。

小学生123 | 2024-05-22 17:09
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

一路同行 2024-05-23 10:04 00 [回复]举报

这样子消防用水量满足要求,但是自喷系统,消火栓系统动压静压可以满足吗?

香.香 2024-05-23 10:06 00 [回复]举报

高位消防水箱里面的水只能满足火灾初期的消防用水量,高位消防水箱不等同于高位消防水池。如果屋顶上设置的消防储水设施能满足火灾延续时间内的消防用水量就可采用常高压消防给水系统。但是这个水量是非常巨大的,对建筑的整体承受力也是很大的,在现实中这种设计非常少。若在每个屋顶设一个高位消防水箱,总的用水量加起来能满足火灾延续时间内的消防用水量,可以不设水泵,所以得根据建筑火灾危险性来计算消防用水量。往往都办不到,一个水池几百m³,一个水箱才几十m³。还有一种情况高层民用建筑采用高位水池供水的高压消防给水系统当储存消防用水量确有困难时,且火灾时能可靠补水时,总容水量可以做室内消防用水量的一半。

胡胡203 2024-05-23 10:47 00 [回复]举报

仅靠一个稳压系统,最不利点的消火栓动压、充实水柱、流量能满足吗?

菜鸟消防 2024-05-23 14:31 00 [回复]举报

《消防给水及消火栓系统技术规范》( GB50974-2014)4.3.11  4 当高层民用建筑采用高位消防水池供水的高压消防给水系统时,高位消防水池储存室内消防用水量确有困难,但火灾时补水可靠,其总有效容积不应小于室内消防用水量的50%。

 我个人的理解:是的,这就是常高压消防系统,但是这样的高位消防水箱要相对高很多、容积要大很多,否则最不利点消火栓没有压力,消火栓栓口动压不符合要求。

 【7.4.12  2  高层建筑、厂房、库房和室内净空高度超过8m的民用建筑等场所,消火栓栓口动压不应小于0.35MPa,且消防水枪充实水柱应按13m计算;其他场所,消火栓栓口动压不应小于0.25MPa,且消防水枪充实水柱应按10m计算。】

南明离火 2024-05-25 16:23 10 [回复]举报

真机智,你水箱底部得再挑高35m就够了~

关闭

关闭

手机APP下载