消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

门斗自然排烟窗

对于门厅的自然排烟,门斗上方的窗户可以作为自然排烟窗吗?北京项目

l123 | 2024-05-06 17:20
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

牛疼 2024-05-07 10:58 00 [回复]举报

是可开启外窗么?

消防网友68723 2024-05-07 11:14 00 [回复]举报

4.3.2 防烟分区内自然排烟窗(口)的面积、数量、位置应按本标准第4.6.3条规定经计算确定,且防烟分区内任一点与最近的自然排烟窗(口)之间的水平距离不应大于30m;

4.3.3 自然排烟窗(口)应设置在排烟区域的顶部或外墙,并应符合下列规定:
    1 当设置在外墙上时,自然排烟窗(口)应在储烟仓以内,但走道、室内空间净高不大于3m的区域的自然排烟窗(口)可设置在室内净高度的1/2以上;
    2 自然排烟窗(口)的开启形式应有利于火灾烟气的排出;
    3 当房间面积不大于200㎡时,自然排烟窗(口)的开启方向可不限;
    4 自然排烟窗(口)宜分散均匀布置,且每组的长度不宜大于3.0m;
    5 设置在防火墙两侧的自然排烟窗(口)之间最近边缘的水平距离不应小于2.0m。

4.3.6 自然排烟窗(口)应设置手动开启装置,设置在高位不便于直接开启的自然排烟窗(口),应设置距地面高度1.3m〜1.5 m的手动开启装置。净空高度大于9m的中庭、建筑面积大于2000㎡的营业厅、展览厅、多功能厅等场所,尚应设置集中手动开启装置和自动开启设施。

南明离火 2024-05-07 17:20 00 [回复]举报

能不能自然排烟  要看是否在最小清晰高度及储烟仓高度以上

gx祥子 2024-05-07 22:45 00 [回复]举报

可开启外窗可以作为自然排烟窗,应在房间净高二分之一以上,最好在储烟仓内。

香.香 2024-05-10 11:45 00 [回复]举报

门斗的作用是用于分隔爆炸区域和非爆炸区域的,有些与爆炸区域相连的楼梯间也设置门斗。所以门斗的作用是护安全的,门斗里面需要防烟而不是排烟。所以很多有爆炸危险的厂房仓库乃至危险区域都是设置的正压送风系统。

潘天坤 2024-06-03 17:16 00 [回复]举报

1、相关规范对于排烟系统的设置条件,没有提到门厅、门斗。

2、 相关规范对于门斗的描述为:有爆炸危险区域内的楼梯间、室外楼梯或有爆炸危险的区域与相邻区域连通处,应设置门斗等防护措施。门斗的隔墙应为耐火极限不应低于2.00h的防火隔墙,门应采用甲级防火门并应与楼梯间的门错位设置。不确定门斗上方的窗户是否有防爆要求及是否可以作为自然排烟设施。

3、建议咨询北京地区设计及审查人员。

4、自然排烟窗一般设置在储烟仓以内(最小清晰高度以上),但走道、室内空间净高不大于3米的区域的自然排烟窗(口)可设置在室内净高度的1/2以上,如果设置高位可开启外窗,还应设置方便开启装置。

关闭

关闭

手机APP下载