消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请教大佬走道排烟的问题。

求教:

项目地址上海。工业研发类。已有项目装饰改造。 高度33m,二类高层。

这是第3层,改造需要,增加了一段走道。原走道机械排烟管距离有些远,接不过来。

问题:此新增的10m长的走道(长10m,宽度2.5m)侧面幕墙有一个电动排烟窗1m2,能满足自然排烟要求吗?可以不做机械排烟吗?如图示:

消防网友75786 | 2024-04-07 14:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

潘天坤 2024-06-17 13:10 00 [回复]举报

新增走道和原有走道之间有挡烟垂壁嘛?

按照烟规51251,如果仅在走道排烟需要在两侧设置各2平方米的有效自然排烟口,现场是否满足,如果不满足需要增设排烟设施。

或者房间是否都满足排烟要求?

关闭

关闭

手机APP下载