请问各位专家,成品白酒的存放有没有相关标准?如有,请提供相关法条依据,谢谢。

龙城金贝贝 | 2024-01-22 14:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

资源网小助理 2024-01-22 14:13 00 [回复]举报

龙城金贝贝   回复: 资源网小助理2024-01-22 16:19

我们不是酒厂呢,酒厂出的成品酒,找我们做仓储装卸,我们应该租赁哪类库房存放?有说丙2,有说丙1,相关规范制度没有特别明确的法条能体现这个消防等级。

0    0 [回复]举报

宾尼   回复: 龙城金贝贝2024-01-22 17:20

0    0 [回复]举报

潘天坤   回复: 龙城金贝贝2024-07-12 19:52

丙1或者甲,不属于丙2

0    0 [回复]举报

阳明心 2024-01-23 09:06 00 [回复]举报

石老师解答:酒精度为38°及以上的白酒储存,其火灾危险性分类与储藏容器的容量及储藏方式相关:

1、以储罐和陶坛等方式储存的白酒库、人工洞白酒库、白酒储罐区、食用酒精库、食用酒精储罐区等,火灾危险性确定为甲类。

2、单瓶容量不大于5L的白酒成品仓库的火灾危险性可划分为丙类1项。

据此,商店及仓库储存的瓶装白酒,火灾危险性类别为丙类(1项),民用建筑内的商店场所(包括超市等),经营存放瓶装白酒并不违反规范要求。但是,商店(商场、超市)等场所仅可以存放销售必需的产品,存放区域应满足相关建筑防火要求。对于较大量贮存的库房性质的存放区域,应按丙类(1项)仓库场所处置,应放置的独立建造的仓库建筑中。

他大爷的 2024-01-23 13:55 00 [回复]举报

如果是瓶装的,丙2类库房就可以