丙二类仓库内允许建小库房吗?

求助各位专家,丙二类的仓库里面打算用砖砌一个300平左右的小库房,里面配气体灭火系统,可行吗?

大队长 | 2024-01-18 14:39
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 8

安洪全 2024-01-19 09:39 00 [回复]举报

库房分区是可以的,分别配置符合要求的自灭系统也是可以的,问题是分出来的300平米小库房存放的物品火灾危险性突不突破丙二类危险性

大队长   回复: 安洪全2024-01-19 14:40

您好,如果仓库的层高是10米,那这个小库房的墙需不需要砌到顶?还是4、5米高也行。

0    0 [回复]举报

安洪全   回复: 大队长2024-01-19 16:30

砌墙的目的是什么?出于安全管理就无所谓,要是防火分隔就是要到顶

0    0 [回复]举报

大队长   回复: 安洪全2024-01-19 17:08

您好,就是分出来的这个300平的小库房的墙体是不是必须要砌筑到顶部,类似于A这样,或者是B那样也可以?顶?

0    0 [回复]举报

南明离火   回复: 大队长2024-01-20 16:09

可以不砌到顶 但是墙体 、楼板(此处楼板应该属于墙体)该满足的耐火极限 都要满足

0    0 [回复]举报

安洪全   回复: 大队长2024-01-22 08:27

如果砌的墙只是为了分隔面积,没有防火分隔的作用,可以不到顶

0    0 [回复]举报

大队长   回复: 安洪全2024-01-25 14:11

好的谢谢。

0    0 [回复]举报

马先生 2024-03-14 14:49 00 [回复]举报

仓库内再分隔一个300m²左右的小库房是可以的;但是不同存放性质的物品,需要用防火隔墙分隔置顶且需要设置消防灭火设施。