请教消防水池取水口问题

请教聂总,如果消防水池是半地下式的,比如地面上下各2m,此时取水口做在顶面显然太高,是否可以在消防水池侧面接出一个室外消火栓,作为消防水的吸水口?从原理上讲,只要吸水高度不大于6m,不管水池内水位是否低于消火栓口,消防车都能从水池吸水。是否可行?

雪原_D1p0 | 2024-01-05 08:52
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

南明离火 2024-01-05 11:24 00 [回复]举报

那个叫取水栓,取水栓的的出水口要低于消防水池最低有效水位,同时做旋流防止器,根据需要做足够的取水栓

雪原_D1p0   回复: 南明离火2024-01-05 14:41

图集是这么画,但是消防车和普通消防水泵是不一样的,消防车是负压吸水,不需要自灌,所以要求出水口低于消防水池最低有效水位不合理,也没有相关规范对此作出规定

0    0 [回复]举报

南明离火   回复: 雪原_D1p02024-01-06 11:14

如果做的是取水栓的话 不自灌 吸不了水吧

0    0 [回复]举报