我在一个化工厂遇见保险单位强制要求常开的消防阀门必须加装锁具锁死消防阀门,避免发生误动作。并且是那种不易开启的锁具。是否符合规范?

V一生何求V | 2023-08-03 14:48
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

安洪全 2023-08-03 16:27 00 [回复]举报

符合。

条文依据包括但不限于:

消防给水及消火栓系统技术规范 GB50974-2014

13.2.6 消防水泵验收应符合下列要求:    

1 消防水泵运转应平稳,应无不良噪声的振动;    

2 工作泵、备用泵、吸水管、出水管及出水管上的泄压阀、水锤消除设施、止回阀、信号阀等的规格、型号、数量,应符合设计要求;吸水管、出水管上的控制阀应锁定在常开位置,并应有明显标记;    

3 消防水泵应采用自灌式引水方式,并应保证全部有效储水被有效利用;    

4 分别开启系统中的每一个末端试水装置、试水阀和试验消火栓,水流指示器、压力开关、压力开关(管网)、高位消防水箱流量开关等信号的功能,均应符合设计要求;    

5 打开消防水泵出水管上试水阀,当采用主电源启动消防水泵时,消防水泵应启动正常;关掉主电源,主、备电源应能正常切换;备用泵启动和相互切换正常;消防水泵就地和远程启停功能应正常;    

6 消防水泵停泵时,水锤消除设施后的压力不应超过水泵出口设计工作压力的1.4倍;    

7 消防水泵启动控制应置于自动启动挡;    

8 采用固定和移动式流量计和压力表测试消防水泵的性能,水泵性能应满足设计要求。    

检查数量:全数检查。    

检查方法:直观检查和采用仪表检测。