消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

计算单元内要求配置的灭火器数量不少于2具,那这两具是否可以分开放置,有无距离要求,还是必须两个在一起?

建筑灭火器配置设计规范 GB50140-2005中6.1.1规定   一个计算单元内配置的灭火器数量不得少于2具,那这两具是否可以分开放置,有无距离要求,还是必须两个在一起?

鼎成大仙 | 2020-12-22 16:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

黄辉 2020-12-22 17:27 00 [回复]举报


本条规定还考虑到在发生火灾时,若能同时使用两具灭火器共同灭火,则对迅速、有效地扑灭初起火灾非常有利。同时,两具灭火器还可起到相互备用的作用,即使其中一具失效,另一具仍可正常使用。英国国家标准也规定对普通楼层,每层灭火器的最少配置数量为2具。


上面的文字为 建筑灭火器配置设计规范 GB50140-2005 6.1.1的条文说明。


2具灭火器放在一起可以互为备用。分开放置,可能会倒置找不到灭火器的。我认为应该放在一起。

WL   回复: 黄辉2025-01-13 10:14

规范是一个计算单元内不少于2具,不是一个设置点不少于2具。你部分截取规范文字来证明自己的观点,是不懂还故意的?

0    0 [回复]举报

刘丽波 2020-12-22 17:35 00 [回复]举报

可以分开设置。每种灭火器都有最大保护距离,计算单元内任一位置都应保护到。

小马 2020-12-22 17:49 00 [回复]举报

看下6.1.1的条文说明,答案显而易见。不过小场所是不讲究这些,

刘丽波 2020-12-23 04:50 10 [回复]举报

规范6.1.1是一个计算单元不少于2具,不是一个配置点不少于2具。一个计算单元可以有多个配置点。

关闭

关闭

手机APP下载