消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

锅炉房到底能否贴邻人密场所

《建筑防火通用规范 GB55037-2022》 

4.1.4 燃油或燃气锅炉、可燃油油浸变压器、充有可燃油的高压电容器和多油开关、柴油发电机房等独立建造的设备用房与民用建筑贴邻时,应采用防火墙分隔,且不应贴邻建筑中人员密集的场所。上述设备用房附设在建筑内时,应符合下列规定:    

1 当位于人员密集的场所的上一层、下一层或贴邻时,应采取防止设备用房的爆炸作用危及上一层、下一层或相邻场所的措施;


条文解释:

当受条件限制需布置在建筑内时,应按本条要求采取相应的防火措施,且不允许设置在建筑中人员聚集的场所的上面、下面或贴邻。


这个到底是允不允许贴临人密呢,为什么 条文和条文解释 完全相反的意思呢;。

消防网友31274 | 2023-04-24 14:25
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 5

陈曲 2023-04-25 08:51 10 [回复]举报

原则上是不允许贴临的 但是你要是现在贴临了就要加措施防止危及人密场所 我是这么理解的  新建建筑就不要琢磨去贴临了

澜沐 2023-04-26 14:39 00 [回复]举报

消防网友31274   回复: 澜沐2023-04-27 11:56

感谢回复,您这个是旧版规范,现在问题是《建筑防火通用规范》条文和条文解释是反着的。有点纠结这个地方。

0    0 [回复]举报

澜沐   回复: 消防网友312742023-04-27 15:06

通用规不是6月1日才开始实施吗,现在用建规还是没有问题的呀?

0    0 [回复]举报

muse3899 2023-12-18 19:50 00 [回复]举报

这个问题应该由资深专家或机构进行文字性答复,因为规范出现这种互相冲突的正文和附文实在不妥。

关闭

关闭

手机APP下载