仓库排烟机房设置什么门和窗?依据是什么?

消防见证 | 2023-04-17 20:46
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

to_rnadoyu 2023-04-18 14:45 00 [回复]举报

甲级防火门,建规6.2.7


to_rnadoyu 2023-04-18 14:46 00 [回复]举报

排烟机房不宜开窗


消防网友78337 2023-04-18 15:06 10 [回复]举报

建筑防烟排烟系统技术标准 GB51251-2017

4.4.5 排烟风机应设置在专用机房内,并应符合本标准第3.3.5条第5款的规定

3.3.5 机械加压送风风机宜采用轴流风机或中、低压离心风机,其设置应符合下列规定:

5 送风机应设置在专用机房内,送风机房并应符合现行国家标准《建筑设计防火规范》GB 50016的规定。


建筑设计防火规范 GB50016-2014(2018年版)

6.2.7 附设在建筑内的消防控制室、灭火设备室、消防水泵房和通风空气调节机房、变配电室等,应采用耐火极限不低于2.00h的防火隔墙和1.50h的楼板与其他部位分隔。     设置在丁、戊类厂房内的通风机房,应采用耐火极限不低于1.00h的防火隔墙和0.50h的楼板与其他部位分隔。     通风、空气调节机房和变配电室开向建筑内的门应采用甲级防火门,消防控制室和其他设备房开向建筑内的门应采用乙级防火门。