建筑的首层扩大封闭楼梯间或者扩大前室能不能存在普通电梯?

请教各位大神,建筑的首层扩大封闭楼梯间或者扩大前室能不能存在普通电梯?按照规范,建筑内首层的其他房间开向扩大封闭楼梯间或者扩大前室的疏散门需要采用乙级防火门,普通电梯的层门耐火极限一般为1小时,那么这样可以满足规范要求吗?

ShaGuo | 2023-02-13 11:17
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

张牙舞爪的张 2023-02-13 20:12 00 [回复]举报

不行,乙级防火门除了防火以外,还有防烟要求。

永锅 2023-02-14 09:05 00 [回复]举报

湖北省建设工程消防设计审查验收疑难问题技术指南(2022年版)

3.5.11条

采用扩大封闭楼梯间、扩大前室(含合用前室)、火灾危险性低且仅作为人员通行的疏散门厅通至室外时,直通室外的门距离疏散楼梯间不超过 30m (从梯段踏步前缘不超过梯段宽度的位置起算)。该疏散门厅应采用不燃材料装修,与门厅连通的配套服务、设备用房应采取耐火极限不低于 3.00h 的防火隔墙、甲级防火门与门厅进行防火分隔;超过 30m 时,应设置避难走道通至室外(附图 3.5.11)。普通电梯可设置在上述疏散门厅,但不宜下至地下室;确需下至地下室时,在地下各层应设置独立的电梯厅,需满足《建筑设计防火规范》第 5.5.6 条的要求。一层普通电梯厅需设置挡烟垂壁和排烟口。

风无心 2023-06-03 19:55 00 [回复]举报

按照建筑设计防火通用规范第7.1.13条,普通电梯设置楼梯前室内需要满足消防电梯的防火性能。