消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟口位置设置

设置机械排烟的场所,是否有规范规定每个防烟分区必须至少设置一个排烟口

周辉锦 | 2022-12-05 22:25
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 7

周家斌 2022-12-06 09:15 70 [回复]举报

没排烟口,烟怎么排出?

周辉锦   回复: 周家斌2022-12-06 09:37

几个相邻防烟分区,有些防烟分区有设,有的没有,但是同属同一防火分区。是大空间餐厅约600平方米,

0    0 [回复]举报

周家斌   回复: 周辉锦2022-12-06 12:38

每个防烟分区必须有的

0    0 [回复]举报

张牙舞爪的张   回复: 周辉锦2022-12-07 13:51

空间高度大于3米不大于6米,防烟分区最大1000平米,长边最大长度36米。综上所述,你这就只算一个防烟分区。

0    0 [回复]举报

消防黄河 2022-12-06 10:09 00 [回复]举报

是的,每个防烟分区必须设机械排烟口,且要满足设置位置和排烟量的要求。

李解不了 2022-12-09 10:26 00 [回复]举报

没有排烟口,怎么排烟?

米米果果 2022-12-15 17:03 00 [回复]举报

每个独立的防烟分区都要设置相应数目的排烟口。


关闭

关闭

手机APP下载