请教一下各位老师,4S店展厅上空配套办公应该按哪条规范执行?

钢铁蜗牛 | 2022-11-28 19:59
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

张牙舞爪的张 2022-11-28 22:05 00 [回复]举报



面积大于两百平米应设两个安全出口;如果附属单多层建筑,疏散距离不大于40米,设置喷淋疏散距离可增加25%。具体详细规范《建规》第五章,民用建筑安全疏散有详细讲解。

钢铁蜗牛   回复: 张牙舞爪的张2022-11-28 22:46

老师你好,配套办公的楼梯是否需要做封闭楼梯间,疏散楼梯首层需要直通室外吗?

0    0 [回复]举报

张牙舞爪的张   回复: 钢铁蜗牛2022-11-28 23:50

你这概括太笼统,无法完全理解。如果该建筑为多层车展的公共建筑,部分楼层是办公室,正常情况下疏散楼梯共用,需要设置封闭楼梯间。楼梯间首层是要直通室外,特殊调整可不限:1、设置扩大封闭楼梯间或防烟楼梯间;2、四层以下未设扩大封闭楼梯间或防烟楼梯间,楼梯间距室外出口距离不大于15米。

0    0 [回复]举报

钢铁蜗牛   回复: 张牙舞爪的张2022-11-29 07:32

了解了,多谢老师解答。

0    0 [回复]举报