各个楼层合用前室加压送风口前是否设置70摄氏度防火阀

各楼层合用前室加压送风口前是否设置70摄氏度防火阀?未见规范条文明确?烟规未提及70℃防火阀?有大神知道哪本规范和条文有明确吗?请告知具体规范条文。谢谢。

清浅 | 2022-11-23 22:40
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

张牙舞爪的张 2022-11-24 08:33 00 [回复]举报

《建规》9.3.11

清浅   回复: 张牙舞爪的张2022-11-24 13:39

这一条貌似没有提到加压送啊

0    0 [回复]举报

张牙舞爪的张   回复: 清浅2022-11-24 16:45

规范要求需要设置防火阀的场所,没有提到就不需要。如果该建筑是防烟楼梯间和防烟楼梯间合用前室,则除机械加压送风口外不能开设任何门窗洞口。

0    0 [回复]举报

好好干 2022-11-24 20:12 10 [回复]举报

建筑防火,9.3.11.3 穿越重要或火灾危险性大的场所的房间隔墙和楼板处;

至于为啥是70℃,你想想70℃的烟气已经很热了,你觉得设置其他温度280度的可合适?

消防黄河 2022-11-25 10:37 00 [回复]举报

不需要。

李哥抓 2022-12-02 18:20 00 [回复]举报

需要设置,

潘天坤 2024-07-01 14:19 00 [回复]举报

建筑设计防火规范 GB50016-2014(2018年版) 第9.3.11条规定:
通风、空气调节系统的风管在下列部位应设置公称动作温度为70℃的防火阀:5 竖向风管与每层水平风管交接处的水平管段上(当建筑内每个防火分区的通风、空气调节系统均独立设置时,水平风管与竖向总管的交接处可不设置防火阀)

建筑防火通用规范 GB55037-2022第6.3.5条规定:通风和空气调节系统的管道、防烟与排烟系统的管道穿过防火墙、防火隔墙、楼板、建筑变形缝处,建筑内未按防火分区独立设置的通风和空气调节系统中的竖向风管与每层水平风管交接的水平管段处均应采取防止火灾通过管道蔓延至其他防火分隔区域的措施
结合条文说明和实施指南来理解,建筑内未按防火分区独立设置的通风和空气调节系统中的竖向风管与每层水平风管交接的水平管段处,应设置防火阀等防火分隔措施并且做好防火保护措施以防止烟气和火势蔓延