自喷系统支架问题?

各位朋友

1、龙门架算不算防晃支架?

2、喷淋系统支管末端的喷头必须设置防晃支架吗?

3、主管的防晃支架采用什么型式的?最好有图有条文

清浅 | 2022-09-22 09:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

Qz 2022-09-23 15:44 00 [回复]举报

1、龙门架不能算防晃支架,

2、末端喷头应该设置防晃支架,根据《自动喷水灭火系统施工及验收规范》第5.1.15的第5条;

3、防晃支架图集详见03S402  P43-45;