石膏板吊顶内的镀锌钢板风管需要做防火处理吗?

安装在楼上独立前室,石膏板吊顶内的镀锌钢板风管,需要做防火处理吗?

安城 | 2021-12-24 18:59
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 6

刘丽波 2021-12-24 21:32 00 [回复]举报

风管类别是哪一类?有耐火极限要求的管道需要做防火包裹,没有的不需要。

安城   回复: 刘丽波2021-12-25 09:00

加压送风风管,在吊顶内,需要做吗?

0    0 [回复]举报

刘丽波   回复: 安城2021-12-25 09:26

需要。

0    0 [回复]举报

消防网友78337 2021-12-25 14:40 00 [回复]举报

你的意思是吊顶本身有耐火性时,风管还需要做防火处理否?


从烟规,3.3.8和4.4.8条看,规范本身就已经考虑了吊顶有耐火性能的问题。


而且已经放宽了要求,在吊顶内风管耐火极限从1小时,降到了0.5小时。


同时要注意,按烟规的规定,和建规的附录标准,参考《通风管道耐火试验方法》GB/T17428-2009,金属风管不能默认为具有0.5小时耐火极限。

杜飞 2021-12-25 23:33 00 [回复]举报

贴5公分岩棉板防热处理。

剑胆琴心 2022-01-11 08:36 00 [回复]举报

这种情况风管是需要做防火处理的,耐火极限不应小于0.5小时,具体可以用涂刷防火涂料、包敷防火板等方式解决。