甲、乙、丙类液体管线穿防火隔墙,需要加设套管么?

甲、乙、丙类液体管线穿防火隔墙,需要加设套管么?

最近发现一个问题,某食堂使用植物油做燃料,油箱放置在单独房间内,燃油管线从隔墙穿过,未加设套管,感觉有一定风险,但查不到规范依据。

Reggie | 2025-06-10 09:50
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 9

小唐12321 2025-06-10 10:12 00 [回复]举报

生物燃料就没国家标准,算丙类吗。


Reggie   回复: 小唐123212025-06-10 12:04

应该是丙类,据相关人员说闪电至少是65

0    0 [回复]举报

小唐12321   回复: Reggie2025-06-11 08:22

很多沿街小商铺随便打个洞就进来,洞都不封。这东西危险性到底怎么样,易挥发吗,挥发后密度怎么样。只知道液体时候不可燃,雾化后才能燃烧。

0    0 [回复]举报

EHS专家-DL 2025-06-10 11:32 00 [回复]举报

应该是需要加套管并封堵严密的。一般植物油认为是丙类液体,根据《消水规》12.3.19-5 消防给水管穿过墙体或楼板时应加设套管..... 消防给水管穿墙都要求加套管,丙类液体穿墙应更严格要求哦。

Reggie   回复: EHS专家-DL2025-06-10 12:55

道理是这样,建筑给水排水及采暖工程施工质量验收规范 GB50242-2002,3.3.13也有加套管要求。


但如果提出整改意见,还是需要明确的规范依据的。


建规中,只有管道穿过变形缝处要加套管。6.3.4

0    0 [回复]举报

牛丫头消防课堂 2025-06-10 22:08 00 [回复]举报

依据《建筑设计防火规范》 GB50016-2014(2018年版)第6.1.5 条防可燃气体和甲、乙、丙类液体的管道严禁穿过防火墙。防火墙内不应设置排气道。

Reggie   回复: 牛丫头消防课堂2025-06-11 10:33

不是穿防火墙

0    0 [回复]举报

李勤 2025-06-12 07:51 00 [回复]举报

牛丫头消防课堂 2025-06-13 10:05 00 [回复]举报

前几年山东省校园、社会福利机构消防安全专项整治的时候,我们发现很多学校、养老院、幼儿园用的那种醇基燃料,提供的报告,有的闪点小于60°,所以看厂家提供的资料,看好与消防相关的参数。