消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

一层临街商铺内室内消火栓来自市政直接供水,室内消火栓压力无法达到规范值,现场没有增压泵,市政管网压力是够的,报告怎么判断?

一层临街商铺内室内消火栓来自市政直接供水,室内消火栓压力无法达到规范值,现场没有增压泵,市政管网压力是够的,报告怎么判断?

消防打工人 | 2025-04-09 16:27
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

资源网小助理 2025-04-09 16:49 00 [回复]举报

7.4.12 室内消火栓栓口压力和消防水枪充实水柱,应符合下列规定:    

1 消火栓栓口动压力不应大于0.50MPa;当大于0.70MPa时必须设置减压装置;    

2 高层建筑、厂房、库房和室内净空高度超过8m的民用建筑等场所,消火栓栓口动压不应小于0.35MPa,且消防水枪充实水柱应按13m计算;其他场所,消火栓栓口动压不应小于0.25MPa,且消防水枪充实水柱应按10m计算。

消防打工人   回复: 资源网小助理2025-04-10 08:24

你说的是单纯的室内消火栓规定,那连着市政的呢?

0    0 [回复]举报

1111111 2025-04-11 08:52 00 [回复]举报

既然市政压力够,大概率是供水管径有问题,不能满足规范要求。建议判定为不符合。

消防打工人   回复: 11111112025-04-11 09:58

市政压力够是满足的市政管网压力0.14,但是达不到室内消火栓的规定。说不符合吧,它连接的是市政,市政达到了0.14,,说符合吧,它实际是室内消火栓,又达不到室内消火栓的规定。

0    0 [回复]举报

李勤 2025-04-11 11:42 00 [回复]举报

历史遗留老建筑采用市政消火栓供水,看他之前是否有验收或其他合法手续,如果有可以判定为合格。比如80年代建设的房屋,当时满足要求,也有合法手续,人家使用性质、法人都没有变化,不能因为规范的更新给他关门,只能建议整改完善。

关闭

关闭

手机APP下载