消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防工作压力问题

设计选用消防加压泵Q=10L/S,H=106m,N=37kw;高位水箱56米高屋面,无稳压泵,泵房负一层,设计工作压力1.43Mpa。请问设计是怎么确定工作压力的,启泵时能达到工作压力吗?

| 2025-03-26 14:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

EHS专家-DL 2025-03-26 15:12 10 [回复]举报

一、设计工作压力的确定依据

  1. 基本计算公式‌:
    根据消防水泵设计扬程的计算公式,设计压力(P)由几何高差(H)和最不利点水灭火设施所需压力(P₀)组成,即:
    P = 0.01H + P₀

    • 几何高差(H)‌:从消防水池最低有效水位至最不利消火栓的垂直高度。假设泵房位于负一层(约-5m),高位水箱在56m屋面,则H = 56m + 5m = 61m(对应0.61MPa)‌。
    • 最不利点压力(P₀)‌:消火栓栓口动压要求为0.35MPa(充实水柱13m)‌。
      因此,理论计算压力为 ‌0.61MPa + 0.35MPa = 0.96MPa‌。
  2. 设计工作压力的调整‌:
    实际设计压力(1.43MPa)高于理论值,可能包含以下修正:

    • 管道阻力损失‌:沿程和局部水头损失需额外增加压力‌。
    • 水泵零流量压力‌:设计工作压力可能参考了水泵零流量时的压力(1.43MPa),叠加水池最低水位与水泵吸水口的静压差(如-0.05MPa),最终系统工作压力为1.43MPa - 0.05MPa = 1.38MPa(接近设计值)‌。

二、启泵时能否达到工作压力的分析

  1. 启动瞬间压力‌:
    消防泵启动时,若流量为零,扬程可达零流量压力(1.43MPa),此时可短暂满足设计工作压力要求‌。

  2. 运行状态压力‌:
    当流量达到额定值(10L/s)时,水泵扬程下降至106m(1.06MPa)。此时需验证系统压力是否满足最不利点需求:

    • 实际可用压力‌:1.06MPa(水泵扬程) - 0.61MPa(几何高差) = 0.45MPa。
    • 对比需求压力‌:0.45MPa > 0.35MPa(消火栓动压要求),表明运行时仍可满足需求‌。
  3. 无稳压泵的影响‌:
    系统依赖高位水箱提供准工作状态压力(56m静压≈0.56MPa)。但消防泵启动后,水箱静压与水泵扬程共同作用,可覆盖初期火灾需求‌。


三、结论

  1. 设计合理性‌:
    设计工作压力1.43MPa综合了零流量压力、几何高差及安全余量,符合规范要求‌。
  2. 启泵可行性‌:
    启动瞬间可达到1.43MPa,但实际运行时需依赖水泵扬程(1.06MPa)与系统阻力平衡,最终仍能满足最不利点压力需求‌。

注:若管道阻力损失或水泵性能偏差较大,需通过实测验证系统实际工况。

关闭

关闭

手机APP下载