消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于消防管道穿越墙体的一些问题

请教各位,消防管道穿越墙体部位需要加设套管,穿越的管道部分什么情况下是需要使用柔性管道,谢谢

消防小萌新 | 2025-02-26 17:29
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

吴宏升 2025-02-27 14:58 00 [回复]举报

地下室

huanglong3721 2025-02-27 15:39 00 [回复]举报

有震动的地方

潘天坤 2025-02-28 08:18 00 [回复]举报

消防水泵的吸水管穿越消防水池时,应采用柔性套管;当消防水泵的吸水管穿越消防水池时采用刚性防水套管时,应在水泵吸水管上设置柔性接头,且管径不应大于DN150


消防给水管穿过墙体或楼板时应加设套管,套管长度不应小于墙体厚度,或应高出楼面或地面50毫米;套管与管道的间隙应采用不燃材料填塞,管道的接口不应位于套管内


消防给水管道不宜穿越建筑基础,当必须穿越时,应采取防护套管等保护措施


消防给水管穿过地下室外墙、构筑物墙壁以及屋面等有防水要求处时,应设防水套管


消防水泵的吸水管、出水管道穿越外墙时,应采用防水套管


钢筋混凝土制作的消防水池和消防水箱的进出水等管道应加设防水套管,钢板等制作的消防水池和消防水箱的进出水等管道宜采用法兰连接,对有振动的管道应加设柔性接头


 当消防水泵和消防水池位于独立的两个基础上且相互为刚性连接时,吸水管上应加设柔性连接管



关闭

关闭

手机APP下载