消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

干式消火栓系统的联动逻辑

一个框架式敞开厂房,报警系统只有手动报警按钮,没有感烟感温探头。采用干式消火栓系统,干管上设置电动阀,在消火栓箱内设置了消火栓箱按钮,用来现场手动启动电动阀。有两个疑惑,1、电动阀除了消火栓箱按钮打开外,还需要联动控制或者手动控制盘控制吗?若需要联动控制,控制逻辑是什么?2、启动消防泵的逻辑,规范要求一个手报+一个烟感或温感+消火栓箱按钮。现场只有手报,是否需要两个手报+一个消火栓箱按钮才能联动启动水泵?一个手报+一个消火栓箱按钮联动启泵,符合要求吗?

苒洋洋 | 2024-12-30 09:50
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

小唐12321 2024-12-30 10:07 00 [回复]举报

个人建议按实用性原则吧,如果有高位水箱,使用流量开关启动水泵,消控室需要多线启动电磁阀与水泵,现场只需要消火栓按钮启动电磁阀。如果需要联动启泵信号就用消火栓按钮加流量开关信号。这个肯定不符合规范就是

苒洋洋   回复: 小唐123212024-12-30 12:34

设置的有高位消防水箱。流量开关肯定直启消防水泵。消控室多线盘能直接启动水泵。现在疑问就是电动阀需不需要多线盘直接控制。电动阀只总线控制符合要求吗?两个手报信号联动开启电动阀,然后电动阀开到位信号+消火栓箱按钮用来联动启动水泵。是否可行及符合规范要求。

0    0 [回复]举报

小唐12321   回复: 苒洋洋2024-12-31 08:36

电磁阀还是要拉直启,毕竟这么关键的东西,模块坏就不能用,启泵有流量开关加消控室直启泵我觉得够了。

0    0 [回复]举报

苒洋洋   回复: 小唐123212024-12-31 14:43

非常感谢。

0    0 [回复]举报

关闭

关闭

手机APP下载