消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟阀执行机构

排烟阀执行机构与排烟口的距离要求

斌哥 | 2024-12-14 10:42
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

潘天坤 2024-12-14 23:19 00 [回复]举报

执行机构说的是风管上的阀体还是手动开启装置?

相关技术规范没有提到排烟口与排烟阀或者手动开启装置的距离要求

一般排烟阀的高度与风管差不多,手动开启装置距地1.3米至1.5米之间,排烟口设置在储烟仓内(清晰高度以上)

磊中 2024-12-16 09:19 00 [回复]举报

我觉得你说的这个执行机构与排烟口的距离没有要求,但应该是在该排烟口所负责的区域内尽量接近排烟口的地方。

清静一念 2024-12-16 14:01 00 [回复]举报

建筑防烟排烟系统技术标准 GB51251-2017

4.4.12- 4 火灾时由火灾自动报警系统联动开启排烟区域的排烟阀或排烟口,应在现场设置手动开启装置。

缱绻一夏 2024-12-17 11:30 00 [回复]举报

排烟阀执行机构到排烟口的距离我记得有不超过6m的要求

阳明心 2024-12-17 13:53 00 [回复]举报

远程执行机构厂家配置的钢丝绳长度有规格,跟阀体的大小有关系,不能太长,太长了拉不动阀体。

关闭

关闭

手机APP下载