消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟风管穿防烟分区需要设置防火阀吗?

地下车库区域,两台排烟风机设置再同一个机房内,分别为同一防火分区的两个防烟分区排烟,其中一台排烟风机的风管穿越防烟分区处是否需要设置280度排烟防火阀?

| 2024-12-11 10:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

金萍 2024-12-11 10:53 00 [回复]举报

需要的

潘天坤 2024-12-11 11:07 00 [回复]举报

请问这个防烟分隔是用实体挡烟垂壁还是实体墙体?

如果属于同一个排烟系统,负担多个防烟分区的排烟支管上或者穿越防火隔墙处,需要设置排烟防火阀

按照楼主的描述,如果两台风机分别自己接风管,并且只负担一个防烟分区,那么应该属于不同系统,不过有时候穿越柔性挡烟垂壁的此区域设计也会额外要求设置(提高要求这样子)



上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据 有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准

LHH2737 2024-12-11 13:53 00 [回复]举报

同一防火分区内可能设置了多个防火单元,如果穿了防火单元就需要,没有穿就不需要

2024-12-11 14:07 00 [回复]举报

收到,非常感谢!

huanglong3721 2024-12-13 15:53 00 [回复]举报


不需要

shijieyang40 2024-12-13 16:05 00 [回复]举报

浙江可不用

EHS专家-DL 2025-03-24 15:39 00 [回复]举报

应该是不需要的。一般防烟分区是按照控制烟气流而设计的,不涉及结构防火,因而同一防火分区,风管穿越防烟分区处不需要需要设置280度排烟防火阀。

关闭

关闭

手机APP下载