消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

超高层建筑水泵设置减压阀,水力警铃不能在90s动作

近期在现场工作中,出现一个问题,导致湿式报警阀组水力警铃不能在90s动作

具体是180米的超高层,为避免地区压力过高,在负一层水泵房管道上设置了减压阀,但出现一个问题—湿式报警阀组水力警铃不能在90s动作,差不多要10分钟水力警铃报警,压力开关动作。怎么解决这个问题。

当初消防给水未采取分区供水,喷淋泵和消火栓泵的扬程均可达到楼顶

 

消防网友50782 | 2021-04-07 21:12
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

牛疼 2021-04-09 11:02 00 [回复]举报

影响水力警铃动作的可能有:1、湿报阀,2、延时器,3、延时器下端的泄水口,4、水力警铃的安装方式是否正确;

一般情况下,水力警铃能够动作,而时间较长的话,说明水压足够,水量不足,因此,请从前三项进行检查。

同时,需要明确,您说的“差不多要10分钟水力警铃报警,压力开关动作。”到底是压开还是警铃动作时间较晚,或是都动作时间较晚。

消防小学生刘振 2022-02-18 15:03 00 [回复]举报

有一种可能就是你水箱间稳压设置的压力过高,管网侧压力大于供水测压力,持续放水管网侧的压力降的很慢,造成阀瓣不能马上打开,也就会造成你水利警铃迟迟不动作。

消防网友33186 2022-11-21 11:47 00 [回复]举报

根据多年施工经验 ,你的减压阀肯定是可调式减压阀! 在水泵不工作状态下,根本不会过去水的!  欢迎讨论!

我还有水箱不往下补水的解决办法!欢迎咨询!

关闭

关闭

手机APP下载