地下商场防火分区

各位老师:关于地下商场(有消防自动报警及灭火系统)防火分区的划分,是按1000平还是2000平算?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

王的MIX4 24-10-24

个人感觉应该归属商店营业厅,且配备喷淋及自动报警系统,按照2000平米设计

0 0 [回复]举报

灿若夏花 24-10-24

满足耐火等级一二,自动灭火,不难装修材料,可以2000,其余地下500,有自喷可以1000

0 0 [回复]举报

LHH2737 24-10-25

按2000,这个问题你现实生活中逛商场的地下部分时应该能感受的到

0 0 [回复]举报

jinyanwu 24-12-04

个人意见,仅供参考:

地下商场,有自动灭火系统,500*2=1000,;

对于地下设备用房,有自动灭火系统,1000*2=2000

这个问题仅针对地下部分,不要过多考虑地上。

0 0 [回复]举报