细水雾灭火系统管道、管件材质要求

细水雾灭火系统技术规范 GB50898-2013 规定:


3.3.10 系统管道应采用冷拔法制造的奥氏体不锈钢钢管,或其他耐腐蚀和耐压性能相当的金属管道。管道的材质和性能应符合现行国家标准《流体输送用不锈钢无缝钢管》GB/T 14976和《流体输送用不锈钢焊接钢管》GB/T 12771的有关规定。


系统最大工作压力不小于3.50MPa时,应采用符合现行国家标准《不锈钢和耐热钢 牌号及化学成分》GB/T 20878中规定牌号为022Cr17Ni12Mo2的奥氏体不锈钢无缝钢管,或其他耐腐蚀和耐压性能不低于牌号为022Cr17Ni12Mo2的金属管道。


3.3.11 系统管道连接件的材质应与管道相同。系统管道宜采用专用接头或法兰连接,也可采用氩弧焊焊接。


3.3.12 系统组件、管道和管道附件的公称压力不应小于系统的最大设计工作压力。对于泵组系统,水泵吸水口至储水箱之间的管道、管道附件、阀门的公称压力,不应小于1.0MPa。


注:022Cr17Ni12Mo2的奥氏体不锈钢,对应的统一数字代号为S31603,即原316L。