一类高层建筑必须选用5/6KG的干粉灭火器吗?4KG可以吗

一类高层建筑必须选用5/6KG的干粉灭火器吗?4KG可以吗

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

安洪全 23-07-10

一类高层建筑的写字楼、公寓是“严重危险级”

严重危险级对应的最低配置基准是“3A”或“89B”

4公斤的干粉对应的是“2A”或“55B”

所以最低5公斤。





0 0 [回复]举报

同同不同   回复: 安洪全23-07-11

正解

0 0 [回复]举报

大树119 23-07-10

规范要求是3A。但是好像基本都是4kg的,好像消防检查也没有去注意这个点,而且我感觉设5 kg好像没必要,甚至有些人都拎不动。

0 0 [回复]举报