消防问答 > 细水雾 提问

高压细水雾的手动控制按钮设置位置

请问各位老师,高压细水雾灭火系统启动方式有自动控制、手动控制和机械应急启动。手动控制,是在消防控制室内按下按钮,开启相应区域控制阀吗? 还是说手动控制的按钮是在各区域控制阀处?

请写下您的回答回答

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 1 回答

安洪全 23-06-26


细水雾灭火系统技术规范 GB50898-2013

3.6.3 在消防控制室内和防护区入口处,应设置系统手动启动装置。

条文说明:

3.6.3 本条规定了对细水雾灭火系统手动控制方式的要求。     系统的手动控制方式,包括控制中心远程控制和防护区就地控制,其设置位置要避免受火灾或环境的危害或易导致误动作,且便于操作。在消防控制室和防护区入口处设置该手动操作装置,可以方便发生火灾时快速启动系统。

1 0 [回复]举报