消防问答 > 气体灭火 提问

气体灭火存储钢瓶接地问题

中国电信、中国移动、中国邮政很多机房,基站现大部分采用有管网或无管网七氟丙烷气体灭火系统。请问那些钢瓶需要接地吗?是否有规范法规等依据?

请写下您的回答回答

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 8 回答

安洪全 23-06-14

气体灭火系统设计规范 GB50370-2005

6.0.6 经过有爆炸危险和变电、配电场所的管网,以及布设在以上场所的金属箱体等,应设防静电接地

0 0 [回复]举报

疑难杂症   回复: 安洪全23-06-14

中国电信、中国移动、中国邮政机房中的气消钢瓶到底要不要接地呢?按6.06中所述通信机房应该是没有爆炸危险,也不属于变电,配电场所,应该不要求接地了。可以这样理解吗?现在甲方要求气消钢瓶接地,我得找个信服的理由说服甲方。

0 0 [回复]举报

安洪全   回复: 疑难杂症23-06-14

甲方之所以提接地的需求,未必是依据消防方面的要求。

如:“建筑电气工程施工质量验收规范 GB50303-2015”


0 0 [回复]举报

疑难杂症   回复: 安洪全23-06-14

甲方已安全理由要求接地,我以消防法规未要求接地为理由不做接地,谁也说服不了谁呀?

0 0 [回复]举报

安洪全   回复: 疑难杂症23-06-14

额,这样您和甲方就会陷入公说公有理,婆说婆有理的无限循环中。


建议您看看合同条款,有无约定验收标准。


有约定的,按约定走,没有约定的能不能增项?

如果不能增项,以后工程能不能多给分配一些。

还要从甲方处结账,以后还要合作,不建议在这事上牵扯太多精力。

0 0 [回复]举报

疑难杂症   回复: 安洪全23-06-15

多谢,答复


0 0 [回复]举报

消防君 23-06-14

七氟丙烷气体不燃不爆,钢瓶接地目的是什么?防止意外触电?如果是为防止意外触电,可在通讯设备上或电箱上设接地

0 0 [回复]举报

安洪全   回复: 消防君23-06-14

可能是防止在喷射时,气体与管网产生静电。

0 0 [回复]举报

最新问题

关闭

关闭