关于电缆桥架下盖板 适用规范问题

大佬们

单层煤粉棚 3W平米左右 电缆桥架下盖板未安装

甲方人员说是为了防止煤粉积聚在线槽内 这个有相应的规范要求吗 另外模块可以直接丢弱电桥架内吗

图片是图纸要求 可忽略不计

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 1 回答

安洪全 23-05-23

我不知道引用的规范和您描述的企业是否匹配,但确实能找到类似应该采取可燃粉尘集聚的说法。

煤化工工程设计防火标准 GB51428-2021

5.3.10 煤储运系统(栈桥除外)、煤粉制备等易积存煤粉的厂房或部位,宜采用不易积粉尘的建筑构造做法,其室内墙面、楼地面应采用光滑、易清洗、不积粉尘的饰面材料。 


但是电缆桥架设置的区域属不属于爆炸危险区域,是不是还要考虑防爆要求?而且没安装盖板属于不积聚的措施,严密封实也是防积聚的措施。



关于模块的问题,其实您用了“直接”这两个字,想必您也觉得不合理。

火灾自动报警系统设计规范 GB50116-2013

6.8.1 每个报警区域内的模块宜相对集中设置在本报警区域内的金属模块箱中