独立的控制室建筑是否需要设置室内消火栓

根据《建筑设计防火规范8.2.1 下列建筑或场所应设置室内消火栓系统:建筑占地面积大于 300m² 的厂房和仓库,工业建筑中控制室可作为设备房考虑,那么占地面积大于300㎡的控制室是否需要设置室内消火栓呢?另外电气火灾明确不宜采用水灭火,这个问题一直纠结,请帮忙解答一下,谢谢
请写下您的回答回答

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 4 回答

刘丽波 20-11-16

需要。控制室内也需要消火栓保护。可以设置为干式的系统。也可以将室内消火栓设置于室外门口附近,保证消火栓可以保护到室内任何部位。

0 0 [回复]举报

一棵松   回复: 刘丽波22-01-28

好的,收到,感谢老师指导

0 0 [回复]举报

易bilibili 20-12-20

从建筑物属性和面积考虑,是应该设置的。如果你从带电火灾考虑的话,可以参考火力发电厂的规范,火力发电厂的控制室也明确要求应设置室内栓。所以综合来说,你说的场所应该设置室内栓

0 0 [回复]举报

一棵松   回复: 易bilibili22-01-28

非常感谢

0 0 [回复]举报