消防问答 > 防烟排烟 提问

排烟口和进风口水平距离是否需要>20m?

同一层同一面外墙上水平布置的机械补风系统的进风口和机械排烟系统的排烟口属于不同的防火分区,那么这两个之间的水平距离是否需要>20m?本人认为不需要,因为发生火灾的起数是按一起来考虑的,也就是说任一防火分区发生火灾,不在同一个防火分区的补风系统和排烟系统只有一个会工作,也就不会岀现烟气被吸入补风口的情况,所以两者之间的距离可以不用考虑,各位老师们怎么看?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 6 回答

Master 22-05-11

火灾会蔓延、烟气到处跑,一栋建筑不是设了防火分隔设施就不蔓延,墙还有烧蹋的时候

2 0 [回复]举报

刘丽波 22-05-11

赞同。

0 0 [回复]举报

老刘头 22-05-12

这里除了补风风机还涉及正压送风风机,规范的规定是考虑最坏的一种情况。绝对是有必要的。在真正发生火灾时,火灾一旦不能在初期得到扑灭,一旦到达猛烈燃烧阶段会迅速突破防火分区的限制。现实中防火分隔物的使用状态能有多少管用的?

0 0 [回复]举报

防消·结合 24-03-07

还是分开点好

0 0 [回复]举报

许迅 24-06-04

个人认为不违规,如果中间完全分隔较好的情况下,可以不用考虑。

如果只是卷帘分隔的情况下,建议还是分开较远距离。原因是在考虑到实际火灾燃烧发展的过程中,现实情况排烟启动较快,防火卷帘尚未降下,将会造成加剧火灾燃烧的效应。不利于火灾控制。

0 0 [回复]举报

影师 24-09-02

需要考虑距离问题,同一防火分区的排烟风机和补风机是需要同时开启的。

0 0 [回复]举报

最新问题

关闭

关闭