消防问答 > 应急照明疏散指示 提问

消防应急照明是否可以兼用日常照明

请教各位,商业建筑内的楼梯间消防应急照明是否可以兼作日常照明,目前设计了一套DC36V的消防应急照明,又设计了一套AC220V的普通照明,基于成本考虑想减少一套,问设计院回复说不可以,查了相关规范,住宅建筑采用自带蓄电池的灯具可以兼用日常照明,商业这块也没说?有没有知道的?

请写下您的回答回答

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 4 回答

吴俊 21-12-28

应急照明可以用于平时照明的,需要购买具有两个单独回路及照明的灯具,里面需要有两组线,一个是普通用电的,还有一个是消防配电线路;消防配电线路不能受开关等控制

0 0 [回复]举报

发条橙子   回复: 吴俊23-10-11

有这种灯具吗


0 0 [回复]举报

阳光哥哥 21-12-31

4 设置在距地面8m及以下的灯具的电压等级及供电方式应符合下列规定:
      1)应选择A型灯具;
      2)地面上设置的标志灯应选择集中电源A型灯具;
      3)未设置消防控制室的住宅建筑,疏散走道、楼梯间等场所可选择自带电源B型灯具。

0 0 [回复]举报

忙里偷闲 22-02-11

《消防应急照明和疏散指示系统技术标准》3.1.6 住宅建筑中,当灯具采用自带蓄电池供电方式时,消防应急照明可以兼用日常照明。商业建筑不可以。

1 0 [回复]举报

最新问题

关闭

关闭