消防问答 > 火灾自动报警 提问

关于消火栓8301模块总报反馈

大家好,问下海湾5000的主机,最近消火栓泵总报反馈,可是现场泵没有动作,(把反馈线挑了还报反馈)总是误报而且自己还恢复,(几乎每天都反馈一次)模块已经换过一次,请问下这是什么原因,该怎么解决

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 6 回答

青春再见 25-06-26

控制柜内部元件问题,比如继电器或者接触器。

或者反馈线的问题,比如潮湿的原因。

0 0 [回复]举报

小唐12321   回复: 青春再见25-06-26

反馈线都拆了,不会,会不会重码了,改个地址码看看

0 0 [回复]举报

李勤 25-06-26

查看线路,怀疑线路、模块有受潮湿部位。

0 0 [回复]举报

EHS专家-DL 25-06-26

大概率是泵控制柜内继电器触点老化可能产生微弱电流泄漏,或继电器复位异常导致虚假反馈信号。另一种可能是主机反馈端口的滤波电路损坏或主板元件老化,可能误解析干扰信号为有效反馈。

解决办法:短接泵控制柜反馈输出端子,若主机仍误报 → 故障点在泵控制柜之后;若不报 → 更换泵控制柜内继电器;

将该模块反馈线临时接入其他正常输入端口,观察是否仍误报,确认原端口是否损坏。

1 0 [回复]举报

徐海金 25-06-26

你查一下线路,多线模块和总线模块,之前一个风机和你一样的情况,总线模块的接线接错了

0 0 [回复]举报

牛丫头消防课堂 25-06-27

看看继电器吧,大概率是继电器节点黏连或者接线松动了。

再就是看看低压压力开关、流量开关是不是一直发出启泵信号。

0 0 [回复]举报