楼梯间是否需要设置乙级防火门并采用封闭楼梯间

单层丙类厂房,办公区域贴邻厂房使用防火墙分隔,办公区域是二层,设置了三座封闭楼梯间并安装了乙级防火门,两座可以直通室外并贴邻外墙,另一座经过大厅通往室外并且贴邻车间防火墙,领导在问能否采用敞开楼梯间?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

牛丫头消防课堂 25-06-05

不允许,因为办公休息区属于厂房这个建筑的一部分,依据《建筑防火通用规范》 GB55037-2022第7.2.2条,多层丙类厂房就应该封闭楼梯间;并没有规范说办公部分楼梯间可以按照民用建筑。

7.2.2 高层厂房和甲、乙、丙类多层厂房的疏散楼梯应为封闭楼梯间或室外楼梯。建筑高度大于32m且任一层使用人数大于10人的厂房,疏散楼梯应为防烟楼梯间或室外楼梯。

0 0 [回复]举报

LHH2737 25-06-06

你有三个封闭楼梯间,可以将其中一个封闭楼梯间改为敞开楼梯间,作为非疏散楼梯使用,但要满足下面的要求:

1、仅剩的两个疏散楼梯依然能满足疏散距离和疏散宽度的设计要求。

2、一至三层防火分区叠加计算没有超过规范规定

0 0 [回复]举报

李勤 25-06-09