消防问答 > 火灾自动报警 提问

消防联动控制线路包括哪些线路?

1、看到《火灾自动报警系统设计规范》GB50116-2013上面11布线-11 .1.1(火灾自动报警系统的传输线路和50V以下供电的控制线路,应采用电压等级不低于300V/500V的铜芯绝缘导线)这里的传输线路是指的报警信号总线Z1、Z2也就是连接探测器、手报、消报、模块的这组线,以及CAN总线和RS485之类的通讯线吗?50V以下供电的控制线路是指经过模块输出的联动24V电源的那一组线吗?

2、《火灾自动报警系统设计规范》GB50116-2013上面11布线-11.2.2(火灾自动报警系统的供电线路、消防联动控制线路应采用耐火铜芯电线,报警总线、消防应急广播和消防专用电话等传输线路应采用阻燃或阻燃耐火电线)这里的供电线路是指给报警主机供电的220V线路以及联动24V供电线路吗?消防联动控制线路是指哪些?上面写了报警总线没有强制规定使用耐火线路,那么意味着报警总线不属于消防联动控制线路。

请各位大佬看清问题帮忙指导一下,谢谢。

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 2 回答

牛丫头消防课堂 25-05-25

你这两个问题,可以合并为一个问题,对11.1.1条来讲,控制线路可能比11.2.2条的消防联动控制线路范围更多些,控制线路可以包含消防联动控制器通过模块控制的线路,也要包括多线盘手动控制线路。因为控制是消防联动系统设置最本质的用途,必须采用耐火电缆;

但是报警线路、广播等线路,一般在火灾初期发挥作用,火灾大了,火灾报警线路意义不大了,所以报警总线、消防应急广播和消防专用电话等传输线路应采用阻燃或阻燃耐火电线要求。其实阻燃耐火要求更高了。

提醒你以下,现在要关注《消防设施通用规范》 GB55036-2022第12.0.16条: 火灾自动报警系统的供电线路、消防联动控制线路应采用燃烧性能不低于B2级的耐火铜芯电线电缆,报警总线、消防应急广播和消防专用电话等传输线路应采用燃烧性能不低于B2级的铜芯电线电缆。

还要关注《民用建筑电气设计标准》 GB51348-2019第13.8.4 条:消防配电线路的选择与敷设,应满足消防用电设备火灾时持续运行时间的要求,并应符合下列规定:    

1 在人员密集场所疏散通道采用的火灾自动报警系统的报警总线,应选择燃烧性能B1级的电线、电缆;其他场所的报警总线应选择燃烧性能不低于B2级的电线、电缆。消防联动总线及联动控制线应选择耐火铜芯电线、电缆。电线、电缆的燃烧性能应符合现行国家标准《 电缆及光缆燃烧性能分级 》GB 31247的规定。

0 0 [回复]举报

EHS专家-DL 25-05-26

1、传输线路包括报警信号总线Z1、Z2以及CAN总线和RS485之类的通讯线;50V以下供电的控制线路是包括经过模块输出的联动24V电源的那一组线。

2、供电线路包含220V主机电源和24V联动电源,均需耐火电缆以确保可靠性;消防联动控制线路特指直接控制消防设备动作的线路(如泵启动、风机控制),需采用耐火铜芯电缆;报警总线不属于消防联动控制线路,报警总线及通信线路属于传输线路,需阻燃或阻燃耐火电缆。

0 0 [回复]举报

最新问题

关闭

关闭