七氟丙烷灭火器有效期

七氟丙烷灭火器有效期时间多长,是3年还是5年就需要进行检测充装。二级甲等医院的,如下图,需要检测和充装吗?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

wetom 25-05-08

七氟丙烷不会过期,至少几十年是没问题的,钢瓶属于压力容器,3-5年需要进行检测。

0 0 [回复]举报

李勤 25-05-09

0 0 [回复]举报

Along Niusk 25-05-12

如二楼所述

要求钢瓶定期检验是特种设备安全技术规程——瓶规的要求:隋5它3

但是瓶规TSG23对消防灭火用气瓶有豁免条款,只需按照特种设备设计和生产,使用维护无要求


但是,消防的国标和行标对此无明确要求,但有官网回复:按照市场监督管理部门要求执行


综上所述,预算充足定期换药,预算不足不换也行

但是,前提是气瓶没有明显的破损、锈蚀、泄漏等影响安全使用的情况,且在20年的生产日期内

0 0 [回复]举报

资源网小助理 25-05-16

参考石老师专题:

气体灭火钢瓶| 检验周期·报废年限·钢印标志·检验资格!

https://b.1190119.com/article-1565.htm

0 0 [回复]举报