消防问答 > 气体灭火 提问

高低压配电室的油浸式变压器室需要设置气体灭火装置吗

厂区建设的独立高低压配电室,一层,在最边的房间设置2间独立的油浸式变压器室,这个需要按《建规》8.3.9条按“其它特殊重要设备室”设置气体灭火装置吗?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 8 回答

徐海金 25-01-23

按建规8.3.8

单台容量在40MV·A及以上的厂矿企业油浸变压器,单台容量在90MV·A及以上的电厂油浸变压器,单台容量在125MV·A及以上的独立变电站油浸变压器;
    2 飞机发动机试验台的试车部位;
    3 充可燃油并设置在高层民用建筑内的高压电容器和多油开关室

0 0 [回复]举报

Kato09   回复: 徐海金25-01-23

应该是按8.3.8条执行,只要不大于40MV·A的就认为就不需要设置自动灭火装置,不管水喷雾或气体灭火。 

不用管高低压配电室是否设置了气体灭火,而也要求合建的单独变压器室也必须设置气体灭火。

0 0 [回复]举报

徐海金   回复: Kato0925-01-24

对,和配电室没啥关系。配电室和变压器室是防火墙分割的。自动灭火一般用排油注氮或水雾系统

0 0 [回复]举报

喧哗 25-01-23

第一种方案:油浸变压器消防设施应该根据建规8.3.8条,一般的油浸变压器都是水喷雾灭火。第二种方案,建规1.0.2条最后一句话,如果属于其他有专门工厂规范的,例如石油化工GB50160,第8.11.3条,可以认为石油化工类的变配电所这个建筑的任何房间,任何情况都不用做水灭火和气体灭火。

0 0 [回复]举报

Kato09   回复: 喧哗25-01-23

不行,现在消防设计审查专家不认这个,我们项目执行的GB50160,厂内设置的变配电室按第8.11.3条也已明确不设置气体及水消防,但是审查意见还是要求按 《建规》8.3.9条执行,让变配电室补充设计气体灭火。

0 0 [回复]举报

潘天坤 25-01-23

关于油浸变压器,建规GB50016有一些要求:单台容量在125MVA及以上的独立变电站油浸变压器应设置自动灭火系统并宜采用水喷雾灭火系统;设置在室内的油浸变压器可采用细水喷雾灭火系统

普通的配电室,一般认为附属在高层民用建筑内(非独立建造的)的配电室属于特殊重要设备室,应设置自动灭火系统,并宜采用气体灭火系统
其他建筑的配电室可以参照执行,不做强制要求,不过有时候设计单位认为一些区域比较重要也会设置自动灭火系统



上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准


1 0 [回复]举报

南明离火   回复: 潘天坤25-02-06

遇到过高层丙类厂房,设计仍然可以变更取消配电房的气体灭火,并通过图审,是否与这个“一般认为附属在高层民用建筑内(非独立建造的)的配电室属于特殊重要设备室”不符

0 0 [回复]举报

潘天坤   回复: 南明离火25-02-06

高层厂房非高层民用建筑,不在规范要求的内容,不过变更系统属于重大变更,可以要求重大变更重新送施工图审查,让审查机构帮忙把关

0 0 [回复]举报

最新问题

关闭

关闭